How to use SAADC to measure 4-20 mA current loop
Sorry for the newbie question but how am I going to use the SAADC to measure 4-20mA current loops? I've used the SAADC to measure temperature, voltage, and resistance but am not sure what input am I expecting from a 4-20mA output source.
Best,
Carlos
  • No, it doesn't, unfortunately. But your suggestions are a good starting point for me to start the code.
    Thanks and best regards.
  • An excitation voltage source is required, the magnitude of which depends on the minimum voltage differential required across the sensor; in the old days that might have been as high as 4 volts drop but now you can probably drive the 4-20mA loop directly from Vdd of 3.3 volts through the sensor and back to Gnd through a (say) 100R resistor. 100R gives 2.0 volts at 20mA, 0.4 volts at 4mA and 0.0 volts in a fault (disconnected) condition. A lower value resistor allows more voltage for the external sensor, but reduces the signal level at the nRF52; 100R (100 Ohm) is often used, but 10R would work fine unless you need maximum signal:noise ratio; 10R at 20mA is 0.2 volts signal. A design goal would normlly allow up to 25mA input so excess voltage monitoring can also be checked, as well as broken-wire (open-circuit).
  • Hi hmolesworth, I appreciate the detailed explanation of requirements to complete a 4-20mA current loop. I will need to ask the vendor who will be the one to supply the excitation voltage.
    Kind regards.